Post by stimarco on Aug 24, 2009 19:16:14 GMT
I suspect this may have come up before, but the Search option only seems to throw up one of my own posts. So...
Is there a technical reason why the Tube network still uses 4th-rail electrification today? I know there used to be issues of current leakage decades ago, but surely these must have been resolved by now?
The mainline railways seem quite happy to run third rail through long, deep tunnels and the Isle of Wight's railway suggests converting existing stock to third rail wouldn't be all that difficult. (If it was, it'd have been cheaper to close the line or convert it to light rail.)
I ask because it would at least reduce the impact of people falling off the platforms at older tube stations. Without the centre live rail, the entire "suicide pit" would be clear of obstructions, for example. Also, I would suspect that a third rail system should be easier to work with and maintain.
Just curious.
|
|
SE13
In memoriam
RIP 23-Oct-2013
Glorious Gooner
Posts: 9,737
|
Post by SE13 on Aug 24, 2009 19:26:20 GMT
|
|
Ben
fotopic... whats that?
Posts: 4,282
|
Post by Ben on Aug 24, 2009 19:51:56 GMT
By and large london still has most of its victorian infrastructure. I suppose therefore that the earth leakage reason is still valid then. Also signalling concernes; making sure the running rail is properly bonded.
Then theres the earthing arguement. Having two live rails means that if one side gets earthed the other jumps up to full voltage so a service can still be run. Least I was told that ages ago; don't know if this is actually the case or not.
It wouldnt ghet rid of an obstruction in the middle either. If you look at Docklands, the ATO wire is in the middle presenting a partial obstruction. This would be the case with the tube in the future.
The IOWs electric infrastructure is nearing the end of its life; theres actually an argument for going 4 rail there.
|
|
Tom
Administrator
Signalfel?
Posts: 4,105
|
Post by Tom on Nov 29, 2009 14:44:23 GMT
With third rail electrification, impedance bonds are required at track circuit boundaries. A lot of LU track circuit boundaries are in platforms and if 3rd rail were to be adopted, a large number of impedance bonds would need to be installed in suicide pits.
|
|
|
Post by djlynch on Nov 29, 2009 20:15:03 GMT
I'd reckon that anyone at 55 Broadway who suggested this would be told it's not worth the expense, even as a big infrastructure project.
There would either have to be massive closures or two conversions - once to third or fourth rail, then again to third rail only once the rolling stock had all been replaced or modified. On top of that, you'd have to do all four subsurface lines (H&C, Circle, Met, District) simultaneously as well as enough of the Piccadilly (Rayners Lane-Uxbridge and South Acton-Barons Court) that you might as well do the entire line.
|
|
Deleted
Deleted Member
Posts: 0
|
Post by Deleted on Nov 29, 2009 21:38:11 GMT
On the plus side if LU ever did adopt 3rd rail electrification there'd be enough spare conductor rail to last a lifetime.
|
|
|
Post by singaporesam on Nov 30, 2009 13:01:51 GMT
Personally, on the rolling stock I´d much rather have negi shoegear over earth brushes any day of the week.
The other big issue here would be EMC , once you start putting traction return current in to the same rails as the Track circuits you need to add much more serious filters on the train to avoid swamping the track circuit, so the line inductor and capacitor size will increase over those currently on the LUL trains which just adds weight for no really good reason.
The EMC study would cost an absolute arm and leg as well, I can just imagine all of the consultants rubbing their hands in lee if this was ever proposed
|
|
|
Post by mikebuzz on Dec 1, 2009 13:47:40 GMT
Had the suburban networks of the mainline companies been included in the LTPB of 1933 as originally intended, this might not be an issue. Then again, they probably would have converted the Southern network to 3rd rail to standardise it.
|
|
|
Post by norbitonflyer on Dec 1, 2009 14:29:15 GMT
Had the suburban networks of the mainline companies been included in the LTPB of 1933 ..... they probably would have converted the Southern network to 3rd rail to standardise it. The Southern network is third rail, and by 1933 it already reached Brighton and Guildford, so converting it would have been a major undertaking. (incidentally, in checking the date, I discovered that Wikipedia thinks that the Underground's 4th rail system is a legacy of the pioneer CSLR! You and I know, of course, that the CSLR did not adopt the four-rail system until 1924, ten years after it joined the UERL Combine. This left the Central (and, after the Met joined LT in 1933, the Northern City) as the only lines left not using the 4-rail system, which they finally adopted in 1940 and 1939 respectively. The W&C was converted to 4-rail shortly before becoming an LT line.
|
|
|
Post by mikebuzz on Dec 1, 2009 15:13:06 GMT
The Southern network is third rail, and by 1933 it already reached Brighton and Guildford, so converting it would have been a major undertaking. Sorry, my mistake, I meant to write ' from 3rd rail'. Shows you were paying attention then! The inclusion of London suburban services of the Big four into the LTPB would not of course have necessitated conversion of 3rd rail as far out as Brighton and the the like.
|
|
Deleted
Deleted Member
Posts: 0
|
Post by Deleted on Dec 1, 2009 15:38:04 GMT
Am I not correct that LUL trains are perfectly happy to work on conventional 3rd rail electrification systems, provided that some arrangement is made to get the negative shoe connected to the neutral runing rails. This can be either by laying a supplementary 4th rail, as on Putney to Wimbledon (or on any other section shared by LUL and BR 3rd rail trains), which unlike on the Underground proper has no direct electrical function but just provides a neutral route, being connected to the running rails. Alternatively the Isle of Wight approach can be to just connect the negative shoe to the wheels in some manner to provide a return path.
As long as the potential difference is 630v it doesn't matter to the train whether this is achieved by +420/-210 in the supply, or +630/neutral.
I believe I am also correct that the whole of the LMS Euston to Watford/Broad Street to Richmond etc network was 4th rail from being laid in the 1920s, up to some time around 1970, when the supply arrangements were changed to normal 3rd rail, and the central conductor rail removed from the parts not shared with the Underground, a change not particularly disruptive to achieve. So there is a precedent for such conversions.
Maybe someone with the technical knowledge can also explain to me (just because I'm interested) what electrical arrangements are needed at places like Putney, where trains pass from one system to another.
|
|
|
Post by norbitonflyer on Dec 1, 2009 16:08:16 GMT
Am I not correct that LUL trains are perfectly happy to work on conventional 3rd rail electrification systems, provided that some arrangement is made to get the negative shoe connected to the neutral runing rails. As long as the potential difference is 630v it doesn't matter to the train whether this is achieved by +420/-210 in the supply, or +630/neutral. Yes it can be done that way, but why bother, unless both types of stock are to run on the same tracks? Unless trains were to run beyond the southern limits of the District or East London lines, (or the Northern was to be extended beyond Morden over the "Wall of Death" to Sutton), there was little scope for interworking. The ELL, although TfL operated, will be 3-rail. The cost of laying a fourth rail throughout the suburban Southern Electric network, and/or adding collector shoes to its rolling stock would have been considerable. And there are safety implications. Had there been a live rail, even at only 210V, between the running rails on the SR, I would probably not be here now! And remember that London Transport operated more than one system from 1913 when it took over the CLR with its central (!) third rail, until 1940 when the line was converted to four-rail. The CSLR (taken over in 1914) was "off-centre" third rail until 1926, and the Northern City, taken over with the Met in 1933, remained with its outside 3rd- and 4th-rail until 1939. (The asymmetric layout was not a problem on either line, as they were both simple shuttles with no possibility of trains being turned) At the places where the District/Bakerloo move from +420/-210 to +630/0, I understand there to be a neutral section. As all trains are made up of more than one unit there is little danger of "gapping". I don't know why the LMR converted the NLL and "dc lines" to 3-rail in c 1971, but it made the takeover by class 313s and 416s easier, ten years later.
|
|
|
Post by mikebuzz on Dec 1, 2009 19:26:06 GMT
Well the CSLR had to wait till after the war and completion of the Central Ealing extension before it was integrated and then it was converted to 4th rail, had its tunnels enlarged, and joined to the Hampstead tube by new sections. The Central London was the exception to the rule, the NCL only joined with the Met in 1933 when the Combine as it was known became a public body, even more corporate than before.
Within 6 years the CL and NCL were converted and the NCL even had tube-sized trains running along it such was the level of standardisation.
If that was the approach of the LPTB (and its predecessor) then it is quite likely suburban lines would have followed suit when upgrades were done either as a cohesive London Suburban section of LT or part of a more integrated network. It is quite possible that the suburban network would have been standardised to 3rd rail as a cohesive unit which of course would include former LNER, LMS and GW lines. Either way, lines joined to the Underground would be converted to 4th rail.
Just to repeat because it doesn't seem to have registered, the government plan was not to incorporate the whole of the southern Railway 3rd rail system into the nascent organisation but to incorporate the suburban network of all 4 mainline companies whether electrified to 3rd rail, 4th rail or not electrified at all. Similarly there was no plan to incorporate 3rd rail services beyond the suburban area.
I would imagine the reason for BR converting the DC network to 3rd rail operation was in order to standardise the network, just as LT has always sought to do.
|
|
Deleted
Deleted Member
Posts: 0
|
Post by Deleted on Dec 2, 2009 1:50:26 GMT
>>the NCL only joined with the Met in 1933 when the Combine as it was known became a public body<<
The Met bought the Northern City in 1913. The reason is not entirely clear, but there were proposals for connecting to the GN at Finsbury Park and to the Met east of Moorgate, to provide some relief on the Widened Lines.
|
|
roythebus
Pleased to say the restoration of BEA coach MLL738 is as complete as it can be, now restoring MLL721
Posts: 1,257
|
Post by roythebus on Dec 2, 2009 9:25:29 GMT
There are indeed neutral sections where the DR meets the BR systems. As the BR network uses the running rails for the return current, they too need to insulated from the LT rails.
On the BR 4-rail sections, the centre rail is bonded to a running rail. I believe the same applies on the Watford DC section from Queens Park.
ISTR the Richmond-Broad Street was similarly wired with the 4th rail bonded to the running rail and was there just because of the through running.
You may remember Sarah Siddons used to work specials on the SR; I gather it was a simple job to convert her to run on 3 rails by lifting the neggy shoes and bonding from there to the chassis! In the early 1970's, Bigal and myself proposed running an R stock tour to Portsmouth or somewhere like that on the southern. As R stock had lifteable neggy shoe gear, it would have been an easy change-over from 4 to 3 rail operation, but it never got much beyond the discussion stage.
On LU, I believe the diffference in potential is that the positive rail is +325v above neutral, the negative rail is -325v belove neutral to give the required 650 volts; on BR, the positive rail is +750v, running rails 0 volts!
I'm not THAT technically minded, but that was the simple explanation given to us as train crews.
I'm not aware of any plans to convert the IoW system to 4 rails. In my view, the expense would not be justified as all the signalling would have to be altered too. If done, it would mean any future stock would not be able to be tested pre-delivery on the main line! More missed phot opportunities.
There was a bit of a "crackpot" plan by the late Fred Ward and others to import used trams from Germany and run them on the Island in the 1990's as trams were being sold off very cheaply. but, like a lot of Fred's plans they came to nothing. Maybe someone should write a book about Fred!
|
|
Deleted
Deleted Member
Posts: 0
|
Post by Deleted on Dec 2, 2009 9:48:52 GMT
More one for the history pages, but on the same subject. Until about 1968 all four platforms on the "suburban" side of Paddington were shared use by the H&C and main line suburban trains, which latter approached from Royal Oak using the same tracks. The old GWR-style Automatic Train Control for repeating signal aspects in the cab had a shoe under the locomotive which physically contacted at signals a ramp between the rails, and this was foul of the Underground 4th rail. So apparently there was a system where the shoe on the steam locomotives, and from about 1960 on the replacing suburban diesel trains, could be lifted before they ran onto the electric lines.
So how did this work then ? This joint running lasted until about 1968, when the tracks into Paddington were fully separated. The old style ATC system was not replaced by the current BR standard system until the 1970s/80s.
|
|
Oracle
In memoriam
RIP 2012
Writing is such sweet sorrow: like heck it is!
Posts: 3,234
|
Post by Oracle on Dec 2, 2009 9:49:15 GMT
Apart from 'Sarah', former Standard Stock used in the then TRC was also converted to run on 3rd rail only when lent to BR. There is a shot in an old Underground News of the TRC at Wimbledon, having been towed there by a battery loco. It was then taken into Wimbledon Depot.
|
|
Ben
fotopic... whats that?
Posts: 4,282
|
Post by Ben on Dec 2, 2009 10:04:31 GMT
And the old Standard Stock rail grinding car; the Pilot motors were converted and the ensemble saw use on the Shepperton branch.
|
|
|
Post by norbitonflyer on Dec 2, 2009 10:08:59 GMT
>>the NCL only joined with the Met in 1933 when the Combine as it was known became a public body<< The Met bought the Northern City in 1913. What I understood him to convey was "the NCL only joined (the Underground), with the Met, in 1933" i.e. the NCL was not part of the Combine until its owner, the Met, joined it in 1933. mikebuzz said " Within 6 years [of creation of London Transport in 1933] the CL and NCL were converted and the NCL even had tube-sized trains running along it such was the level of standardisation." All three lines even used "Standard" stock after conversion! I think the more significant factor in the date of conversion in all three cases was that the original rolling stock was life-expired, at over 35 years old, and that, in the case of the CSLR, it was to be joined to the Hampstead Tube, and in the other two, Standard stock was available to replace the original stock, as the new 1938 stock came on stream elsewhere. (Incidentally, why did the Central get cascaded Standard stock instead of new 1938 stock?) Note that the UERL did build some stock with non-standard current collecton: the Central's Ealing extension was opened in 1920, and new stock suitable for open-air running was built for it.
|
|
|
Post by mikebuzz on Dec 2, 2009 16:43:43 GMT
One could imagine that had the suburban network been incorporated and an attempt at standardisation made that it would have taken a very long time to convert to 4th rail as it is clear that there were limits on how much could be done at any one time. It is more likely that an attempt would have been made to standardise the suburban network to 3rd rail as and when it was expedient and an electrification program would have been considered as part of it. There wasn't much at the time to convert. Whether or not the sub-surface lines would have been considered for conversion is another matter. >>the NCL only joined with the Met in 1933 when the Combine as it was known became a public body<< The Met bought the Northern City in 1913. The reason is not entirely clear, but there were proposals for connecting to the GN at Finsbury Park and to the Met east of Moorgate, to provide some relief on the Widened Lines. The Met didn't want the GNR getting its hands on the ailing GN&C as it benefited from the mainline companies use of its Moorgate terminus. GN use of the widened lines amounted to a tidy sum in rent annually. The Met managed to get hold of the GN&C but the LER were interested too - at this time they became the combine taking over the Central London and the C&SLR. The Met and LER made an agreement whereby the Met could have the GN&C provided they didn't extend it north (the LER wanted the Pic to go that way) in return for the LER not extending the C&SLR along the northern circle. This should be in historical IMO.
|
|